I.ve been trying to trace a fault on a lighting circuit where a voltage of 3v is present when the lamps are switched off. I have switched off breakers in turn and discovered that when the ring final circuit is switched off the 3v dissapears from the lighting circuit. I'm thinking along the lines of borrowed neutral somewhere but will need floors to come up to find JB's. The lighting circuit is in need of rewiring as it's old rubber insulation and it is perishing. Just waiting for client to say what they want to do. If it was my house then I would rewire it.
ray
3V on a circuit while lamps are switched off??
This is NOT a fault.. :C
sounds more like normal characteristics of an electrical installation where multiple live cables are in close proximity to each other..
often running for several meters under floors, above ceilings through joists..
and using a cheap electronic multimeter.
The technical reason is to do with electro magnetic effects inducing voltages from one cable to another..
and the fact that the multimeter doesn't put any real load on your cable to consume the induced voltage.
e.g.
I just got an off-cut of 1.5mm T&E rested it by some ring main cables and I got "6v" between the live and a near by water pipe..
and 1.5v if the cable was just lying on the floor!
At all times both ends of the cable are just lying open not connected!!!
similar principle to Radio & TV aerials picking up signals in the air and inducing voltages onto the antenna down lead
3V is not likely to be any fault.
:|