OK,
I'll be honest, I've not got this running yet.
Another guy has had a go, and fixed part of the fault.
Single motor machine, DOL, 1ph.
3 contactor starter.
Start, run & capacitor contactors.
Start & run, electrically interlocked.
Starter operates fine without motor connected.
i.e. goes through the required contactor status.
I have yet to check the o.p. voltages of the starter.
I have a drawing of the starter, very poor, as is the wiring, no colour coding, or numbering.
The motor has 3 sets of windings.
Z1/Z2, R = 2.4 ohms
U1/U2, R = 1.0 ohms
U5/U6, R = 1.4 ohms
No rating plate on motor, or any motor rating info on drg.
All insulation resistances between windings & to earth >500M ohms on motor & cable to motor.
Supply cable tests OK on IR & continuity also.
No RCD's involved to simplify things.
Motor will not run up to speed, and upon change over from start to run, trips mcb, B20, which it was running on fine.
Manual changeover on release of start button.
Motor wired to drawing, as long as winding tails in motor are correct.
Starter & motor wired to drawing.
No mechanical issues.
Caps are 100 uF each and test OK alone & in parallel which is how they are wired in starter, both for capacitance, and as far as I can tell ESR.
I don't have an AT31/33, anyone?...
I need ideas for a quick fix.
I'm the 2nd person to check this out, 1st guy was very familiar with machines too!
It has already had 3 new contactors & aux's.
Had not found any wiring issues with the previous repairs.
Suggestions...
I'll be honest, I've not got this running yet.
Another guy has had a go, and fixed part of the fault.
Single motor machine, DOL, 1ph.
3 contactor starter.
Start, run & capacitor contactors.
Start & run, electrically interlocked.
Starter operates fine without motor connected.
i.e. goes through the required contactor status.
I have yet to check the o.p. voltages of the starter.
I have a drawing of the starter, very poor, as is the wiring, no colour coding, or numbering.
The motor has 3 sets of windings.
Z1/Z2, R = 2.4 ohms
U1/U2, R = 1.0 ohms
U5/U6, R = 1.4 ohms
No rating plate on motor, or any motor rating info on drg.
All insulation resistances between windings & to earth >500M ohms on motor & cable to motor.
Supply cable tests OK on IR & continuity also.
No RCD's involved to simplify things.
Motor will not run up to speed, and upon change over from start to run, trips mcb, B20, which it was running on fine.
Manual changeover on release of start button.
Motor wired to drawing, as long as winding tails in motor are correct.
Starter & motor wired to drawing.
No mechanical issues.
Caps are 100 uF each and test OK alone & in parallel which is how they are wired in starter, both for capacitance, and as far as I can tell ESR.
I don't have an AT31/33, anyone?...
I need ideas for a quick fix.
I'm the 2nd person to check this out, 1st guy was very familiar with machines too!
It has already had 3 new contactors & aux's.
Had not found any wiring issues with the previous repairs.
Suggestions...