So here's a thought to ponder....
Amongst doing "other work" on a job today..
asked to look as some garden lights that no longer work...
There are Five of these sort of metal 230V GU10 lamps that stick in the ground on a spike..
Bit like these: https://www.tlc-direct.co.uk/Products/GLGU10SPIKE.html
Found one external box where SWA connects to lamp flex..
But as for where the other 4 lamps connect onto the supply is anybody's guess.!?
Bottom line is that if 'power is turned on' customer said it trips the fuse box...
IR test gives 0.0Meg ohms @ 230V.. Live->Earth (and Neutral->Earth)
Couldn't find any of the other boxes..
So for the time being.. both Live & Neutral disconnected at the fuse box awaiting further investigations...
Some of the lamps did have damp and cr4p inside....
But my other thoughts were to issues of "Exporting Earth"....
I assume these metal fittings are also earthed via the spike that sticks in the ground.....
Didn't have time (or couldn't be arsed to actually check earth continuity to the spike, as the lights didn't work anyway!)..
BUT....
supply is TN-C-S
So in effect we have...
TN-C-S to all the internal house electrics..
Plus 1.5mm SWA supplying 5x mini-earth rods part of GU10 spot lamps stuffed in the garden....
SO....
in the event of fault conditions the garden lights supply could be taking a proportion of the full fault current divided between other bonding..
(taking in to account that the incoming water is plastic!) and the garden lights.are all metal..... !
Bit concerning re: designed & installed by garden landscapers several years ago!!
:C
Amongst doing "other work" on a job today..
asked to look as some garden lights that no longer work...
There are Five of these sort of metal 230V GU10 lamps that stick in the ground on a spike..
Bit like these: https://www.tlc-direct.co.uk/Products/GLGU10SPIKE.html
Found one external box where SWA connects to lamp flex..
But as for where the other 4 lamps connect onto the supply is anybody's guess.!?
Bottom line is that if 'power is turned on' customer said it trips the fuse box...
IR test gives 0.0Meg ohms @ 230V.. Live->Earth (and Neutral->Earth)
Couldn't find any of the other boxes..
So for the time being.. both Live & Neutral disconnected at the fuse box awaiting further investigations...
Some of the lamps did have damp and cr4p inside....
But my other thoughts were to issues of "Exporting Earth"....
I assume these metal fittings are also earthed via the spike that sticks in the ground.....
Didn't have time (or couldn't be arsed to actually check earth continuity to the spike, as the lights didn't work anyway!)..
BUT....
supply is TN-C-S
So in effect we have...
TN-C-S to all the internal house electrics..
Plus 1.5mm SWA supplying 5x mini-earth rods part of GU10 spot lamps stuffed in the garden....
SO....
in the event of fault conditions the garden lights supply could be taking a proportion of the full fault current divided between other bonding..
(taking in to account that the incoming water is plastic!) and the garden lights.are all metal..... !
Bit concerning re: designed & installed by garden landscapers several years ago!!
:C