Hi,
I would appreciate some thoughts on this! Site has a 42 way industrial board fed by 3 core 10mm wire armoured sub main. Ze at the board was 0.60ohms, the sub main must be 60 mts long as it is fed from the mains position in a neighbouring building.
The DB has an earth electrode and bonding to both gas and structural steel work, I didn't disconnect these when testing for ZE for access and practical readings! The DB [Hager] has a 100A 30ma main switch controlling everything in the workshop. Clerly when there is a fault everything goes out, not a great scenario.
What I proposed to do was to change the main 30ma for a 300ma time deayed one and then change the MCB's for RCBO's to protect the circuits that need them. I think that seems a reasonable solution that meets the regs but the difficulty is is that there are 3 phase mcb's, about 6 from memory and most of them are to sockets, so will need 30 ma protection. Hager don't do 3 phase RCBO's and for a whole range of reasons i don't want to rewire all this lot to a separate board. Does anyone have any ideae what I could use in the board for 3 P RCBO's...?!
Cheers
I would appreciate some thoughts on this! Site has a 42 way industrial board fed by 3 core 10mm wire armoured sub main. Ze at the board was 0.60ohms, the sub main must be 60 mts long as it is fed from the mains position in a neighbouring building.
The DB has an earth electrode and bonding to both gas and structural steel work, I didn't disconnect these when testing for ZE for access and practical readings! The DB [Hager] has a 100A 30ma main switch controlling everything in the workshop. Clerly when there is a fault everything goes out, not a great scenario.
What I proposed to do was to change the main 30ma for a 300ma time deayed one and then change the MCB's for RCBO's to protect the circuits that need them. I think that seems a reasonable solution that meets the regs but the difficulty is is that there are 3 phase mcb's, about 6 from memory and most of them are to sockets, so will need 30 ma protection. Hager don't do 3 phase RCBO's and for a whole range of reasons i don't want to rewire all this lot to a separate board. Does anyone have any ideae what I could use in the board for 3 P RCBO's...?!
Cheers