Motor MCCB

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

Loyal

Junior Member
Joined
May 17, 2010
Messages
16
Reaction score
0
I have a question about sizing MCCB for motor. If a 22 kW motor has a full load current of 42A and a starting current of 250A, then what should the trip setting of the MCCB be? I can use an MCCB with a frame size of 100A, but not sure about the trip setting. Is there some general rule to select the trip setting (for example 1.4*full-load-current.)

 
What sort of circuit breaker?

The really decent ones have different settings for thermal and magnetic trip currents. Set the thermal trip current to 42A and the magnetic trip to 250A

 
you rate the mcb to just above FLC a type d

you won't be using a mccb for that low current

what are you using for starting?

 
Motor is used for centrifugal pump.

If I rate the magnetic trip to just above FLC (say 50A), then will it withstand the high starting current?

Magnetic Trip of 250A is too high as the maximum frame size is 100A.

 
Motor is used for centrifugal pump. If I rate the magnetic trip to just above FLC (say 50A), then will it withstand the high starting current?

Magnetic Trip of 250A is too high as the maximum frame size is 100A.
an mccb will have type d characteristics so it will resist the urge to trip for an extended period for instantaneous over currents(still relatively small in time) than a type b or c etc

so yes

 
The problem is that we don't have MCB, we have MCCB. Is the trip setting just above FLC ok for MCCB as well?

 
Oh sorry, never mind, I see Lostit's response now about MCCB being similar to type D MCB.

 
The problem is that we don't have MCB, we have MCCB. Is the trip setting just above FLC ok for MCCB as well?
you need some head way as you want the overload in the starter to be tripping for overloads not the mccb.

so yes set the mccb above the overload setting

 
That's the whole point. The thermal trip is the longer term average current, so you set that to match the FLC and it will withstand the start up current.

The magnetic trip is near instantaneous, so you set that as low as you can get away with without nuisance tripping at start up. If you say the start current is 250A than that's what it needs to be. Where did your 250A figure come from? measurement or guestimate?

 
At 22kW SURELY you'd have that on a star/delta starter.

The start current & running current would then be proportional to the winding configuration.

Take the TM overloads used in starters, they will be sized differently for DOL & Y/D starters, so your MCCB selection & settings are not totaly B&W.

You could clamp the LRC of the motor to get an idea of the max current draw?

HTH

 
As above , probably star/delta so start load will be lower . An MCCB is not needed but type C or D . I would guess type C 50amp TP MCB .

Phone Crabtree Techical or similar , they're the experts.

I presume it has to be an MCB ?? HRC fuses are far better in industry ,IMHO.

 
Thinking about this my instinct would be a 50A or possibly a 63A C or D curve MCB.

As Deke says MCCB not necessary, but if you have a panel board that won't take an MCB you may have no choice.

the selection would depend on the mechanical inertia of the load.

A large mechanical inertia, thus a long transition time would need a different supply characteristic to a small mechanical load with a short transition time, and also, if the Y/D is set up correctly this would help.

HRC's can help, you may need gM's though.

To get Zs for gM's you need manuf' data oficially.

Another thing to think about is if it is Y/D is is open or closed transition?

This will have an affect on the change over current.

 
If its a star delta starter, the overload markings will relate to direct on line

So set it to motor current x 0.58

 
Ok

For a star delta overload setting EVEN if the overload has been supplied downrated the answer will still be the same

ie a 40a motor x0.58 = 23.2 amps

so the overload would be set at around 23 amps

so if the overload has been supplied downrated - say 17-25 amps, you would still select 23 amps

If you have been supplied a 30-40a overload, then you cant select 23a

If you have been supplied a 12-18a overload then you cant select 23a

When i buy starters from the wholesaler they

1) select the starter, DOL,Reversing,Star Delta etc

2) select the overload

The overload is in effect the same item for each starter, however getting the correct one is simply the selection of the current rating for the application

They do not have DOL overloads on one shelf and Star Delta overloads on a different shelf - they simply have the one range to pick from

Correct selection is the answer

Hence the x0.58 advice

 
300,

22kW FLC 42 - 45A (typically)

Y/D rating (@0.58) 24 - 26A (typically)

Thus my comment applies as I did not contradict your formula, I merely warned that the situation may arise where the O/L may not cover the correct range as one MAY order an O/L rated for DOL and fit to a Y/D starter!

Thus you have merely confirmed my point!

Selection of the O/L device must be correct for the starting mode.

BTW I'd never put a 22kW induction motor on DOL no matter what the external load really!

 
Let me re-phrase my problem:

To avoid confusion, let's take a large motor for which we can only use MCCB (not MCB). let's say 110 kW DOL motor. The Schneider's recommended combination is: magnetic only breaker (NSX250HMA220) plus contactor (LC1F225) plus overload (LRD05.)

The motor FLC is 200A, and let's assume the starting current is 1000A.

Now here is my problem:

How can I set the magnetic trip to 1000A, while the maximum breaker frame size is 250A?

 
Loyal,

First you'll never start a 110kW motor on a DOL starter!

Sorry the Q is flawed.

However, I'll have a go!

Why do you want to set the mag to 1kA?

Your starting current will be very short duration, so yes it will affect the M section rather than the T section of the MCCB.

You may have a max breaker frame of 250A, you wouls set the T & M dials to a proportion of the breaker rating, say 200A breaker you would set the "dials" according to the manuf' & designers specs for the system.

These would depend on many things, motor design specs, breaker design, cables, external motor load, supply characteristics etc. etc. etc.

HTH

 
and that an LRD05 only fits contactors up to 32a, and has a setting of 0.63 - 1.0 A

I know its irrelevent really, just suprised to see that part number pop up in the combination of kit

:coat

 