I tend to re-fit 20A MCBs except in in high useage areas like kitchens, and certainly carry a few spares just in caseWith regard to cu upgrades when testing, i take it all faults must be rectified as its an eic you fill out? doing one over tonight and tommorrow night and i have 2 32 amp mcbs with 3 and 2 cables in, none being a ring!! arrgghhhh
But if you are changing a consumer unit there should be no need to double up circuits.yeah i refit 20a mcbs, I know its ok to double up on mcbs but what do you record on your test sheets as realistically its 2 seperate circuits? I tested them both, and recorded both results, but when it comes to the test sheets with only one row for that mcb what do you write down? common sence would tell me to write down the one with the higher zs. or lower IR readings, etc
I also hate the nice little ring with fairly low r1,r2&rn then when you measure R1+R2 they are well off where someone has decided to spur a radial off the ring still in 2.5mm still on a nice 30A fuse or 32A breaker. I treat them as a radial and drop the new MCB to something more realistic (20A or even 16A).With regard to cu upgrades when testing, i take it all faults must be rectified as its an eic you fill out? doing one over tonight and tommorrow night and i have 2 32 amp mcbs with 3 and 2 cables in, none being a ring!! arrgghhhh