Nusiance Rcd Tripping

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

toml

Junior Member
Joined
Jun 21, 2010
Messages
65
Reaction score
0
Been toa job this morning and the customer (well gaffer) is complaining about nusiance tripping. Meggered it all, all fine (over 150meg for a10yr old installation). 2 rcd tested on auto 1 tested at 1x 17 and 5x 8ms. But the other one doesn't trip at all for the tester but trip about 3 or 4 times a day for no reason) I plan to replace it tomorrow (if I can get hold of a legrande rcd from anywhere)

But if it's not thus then what can it be. Also next door is suffering from the same problem which I've looked at and again the wiring is fine

Any ideas?

 
Ramp tested. One trips at 17mA and the dodgy one trips at >33mA. So I'm hoping it's that

 
Are you testing them with loads disconnected?

2x RCD's...  one working one tripping... 

why not swap them over first to see if the problem stays with the RCD or with the circuits?

Next door having problems as well.....

What is the earting arrangement ...

Whats your  Ze / Ra?

Could you have something from outside your installation causing problems..?

:popcorn

 
It's a tt system, ra is 23.9 ohms. I'm replacing the rcd for the piece of mind of me gaffer. Then if it ain't then I will suggest that central power or whoever they are these days comes and has a look

 
So is there also a front end 100ma td RCD, has there been any tripping issues with that? 

Doc H.

 