What is happening, everything is going wrong.
So you guys might already know that I had to change my inverters as I was struggling to find compatible batteries, so I bought a full system from AllGreen Energy.
I thought I'd check the input stats, as the PV Amps were right on the limit with the other inverters, and I stupidly didn't think of this before, as I just thought a 6kw inverter would be fine with a 6kw array.
Now my panels are 400w, at 10.5A, and the inverter max input is 18.5A per string, so this is absolutely fine.
My issue is the voltage. The inverters say Max PV voltage 550V, and Full MPPT range 170v to 500v. My panels are 38.1V each, with two strings of 8 panels giving me 305V per string, 610V total.
All stats for both panels and inverter are attached as screenshots.
Am I screwed?
So you guys might already know that I had to change my inverters as I was struggling to find compatible batteries, so I bought a full system from AllGreen Energy.
I thought I'd check the input stats, as the PV Amps were right on the limit with the other inverters, and I stupidly didn't think of this before, as I just thought a 6kw inverter would be fine with a 6kw array.
Now my panels are 400w, at 10.5A, and the inverter max input is 18.5A per string, so this is absolutely fine.
My issue is the voltage. The inverters say Max PV voltage 550V, and Full MPPT range 170v to 500v. My panels are 38.1V each, with two strings of 8 panels giving me 305V per string, 610V total.
All stats for both panels and inverter are attached as screenshots.
Am I screwed?