I just need some opinions for calculating my demand.
I've put my estimate in for a building which is to be converted into 5x Bedsits/flats. Each one of the unit is to have the following
Shower - 40A circuit, 10mm, 9.5kw.
Cooker - 32A circuit, 6mm, 6kw.
Sockets - 32A circuit, ring final
lights - 6A circuits, 1.5mm, 4x100w assumed
smokes - 6A
Calculating rule of thumb that DNO's use adding the breaker sizes up then multiplying by 0.4 = Demand is 46.4A. mmmmmm!!
Using OSG for diversity:
Shower - 100% FL = 39.5A
Cooker - 10A + 30% remainder of current = 14.5A
Sockets - Rated current of circuit = 32A (which is impossible imo!)
Lights - 66% of total current demand = 1.6A (negligible)
Smokes - 1A max! (negligible!)
So worst case using OSG would be 88.6A
Now to me, a single person living in the bedsit will not use the demand as they wont be showering, cooking, watching TV etc etc all at once!
Would we assume a % of full load? Maybe 75% which would make it 66.45A
Trouble being is that the supply needs upgrading and Northern Power Grid are asking for total demand in kVA which works out at:
kVA= V x I / 1000 (single phase) = 240 x 88.6 / 1000 = 21.2kVA or 240 x 66.45 / 1000 = 15.95kVA
Now I've advised them that they NEED a 3 phase supply to be installed but was just wanting the opinions of the more experienced designers amongst us please.
mucho grassy a r s e.
I've put my estimate in for a building which is to be converted into 5x Bedsits/flats. Each one of the unit is to have the following
Shower - 40A circuit, 10mm, 9.5kw.
Cooker - 32A circuit, 6mm, 6kw.
Sockets - 32A circuit, ring final
lights - 6A circuits, 1.5mm, 4x100w assumed
smokes - 6A
Calculating rule of thumb that DNO's use adding the breaker sizes up then multiplying by 0.4 = Demand is 46.4A. mmmmmm!!
Using OSG for diversity:
Shower - 100% FL = 39.5A
Cooker - 10A + 30% remainder of current = 14.5A
Sockets - Rated current of circuit = 32A (which is impossible imo!)
Lights - 66% of total current demand = 1.6A (negligible)
Smokes - 1A max! (negligible!)
So worst case using OSG would be 88.6A
Now to me, a single person living in the bedsit will not use the demand as they wont be showering, cooking, watching TV etc etc all at once!
Would we assume a % of full load? Maybe 75% which would make it 66.45A
Trouble being is that the supply needs upgrading and Northern Power Grid are asking for total demand in kVA which works out at:
kVA= V x I / 1000 (single phase) = 240 x 88.6 / 1000 = 21.2kVA or 240 x 66.45 / 1000 = 15.95kVA
Now I've advised them that they NEED a 3 phase supply to be installed but was just wanting the opinions of the more experienced designers amongst us please.
mucho grassy a r s e.