I have to quote for a job to supply power from a house to a garage and a summer house. Neither the garage nor summerhouse has any extraneous metal. Garage is 15m from the house and the summer house is 10m from the garage.
There are two modern Wylex consumer units in the house - one is protected by one 30ma RCD covering all ways and the other does not have any RCD protection but is fitted out with RCBOs. There are spare ways in both consumer units.
Earthing is TT. Zs at a downstairs socket in the house is 67Ω.
My plan is to run 6mm2 3 core SWA connected to a plastic adaptable box with the cable earth core insulated from a spare way in the non RCD consumer unit from a 40A breaker
At the garage end I plan to install a metal consumer unit with a 30ma RCD covering all ways with its own earth spike and terminate the SWA in the consumer unit. The plan is to connect together the armouring and the earth core of the SWA at the garage consumer unit and connect these to the earth bar in the consumer unit.
I then plan to run a 2.5mm2 SWA from the garage consumer unit with a 20A breaker to the Summer House and terminate it in a metal box (again with the armouring and earth core connected together) and then run T&E cable to three sockets and two lights with an FCU to protect the lights.
I have assumed a maximum load for the garage and summer house as 2kW each.
I realise that there are issues with contention of RCDs and equipotential zones.
My questions are:-
Have I used the right approach with connecting the armouring and the earth core of the SWA?
Should be SWA be protected by an RCD at the house consumer unit end despite the contention problems that this would pose?
Is the earthing satisfactory in the Summer House?
There are two modern Wylex consumer units in the house - one is protected by one 30ma RCD covering all ways and the other does not have any RCD protection but is fitted out with RCBOs. There are spare ways in both consumer units.
Earthing is TT. Zs at a downstairs socket in the house is 67Ω.
My plan is to run 6mm2 3 core SWA connected to a plastic adaptable box with the cable earth core insulated from a spare way in the non RCD consumer unit from a 40A breaker
At the garage end I plan to install a metal consumer unit with a 30ma RCD covering all ways with its own earth spike and terminate the SWA in the consumer unit. The plan is to connect together the armouring and the earth core of the SWA at the garage consumer unit and connect these to the earth bar in the consumer unit.
I then plan to run a 2.5mm2 SWA from the garage consumer unit with a 20A breaker to the Summer House and terminate it in a metal box (again with the armouring and earth core connected together) and then run T&E cable to three sockets and two lights with an FCU to protect the lights.
I have assumed a maximum load for the garage and summer house as 2kW each.
I realise that there are issues with contention of RCDs and equipotential zones.
My questions are:-
Have I used the right approach with connecting the armouring and the earth core of the SWA?
Should be SWA be protected by an RCD at the house consumer unit end despite the contention problems that this would pose?
Is the earthing satisfactory in the Summer House?