Can anyone offer a little advice on what coding I should give the following, I've put what I'm thinking of giving but I would appreciate a little help from those with greater knowledge and experience.
Rubber wiring from con unit to cooker point - IR was 299M ohms L-N, L-E, N-E. r1+r2=o.06 no visible sign of insulation breaking down - 4
Rubber wiring from con unit to socket outlet - IR was 2.91M ohms L-E, 184M ohms N-E and L-N, r1+r2 =0.32. there was evidence of the insulation breaking down behind a socket face - 2
Consumer units (2) not fastened to wall 2
Cooker hood feed in 2.5 mm T/E taken directly from cooker plate switch to a junction box, to hood. Not fused. (Radial to cooker protected by 30A bs 3036 fuse - 2
Downlighters in kitchen ceiling next to ceiling joists (as in 2/3 mm from the joists) and covered with insulation. (No signs yet of heat damage - only put in december 2010) - 2
The customer had the kitchen and bathroom refurbished Dec 2010. There are no certificates for the work (surprise, surprise having seen the work). The electric shower does not have RCD protection nor is there any bonding in the bathroom. The bathroom also has 2 downlighters fitted. The builder has re used some of the existing rubber insulated cables which look to be around 40-50 yrs old. Will try for some pictures later.
Thanks for any advice
Rubber wiring from con unit to cooker point - IR was 299M ohms L-N, L-E, N-E. r1+r2=o.06 no visible sign of insulation breaking down - 4
Rubber wiring from con unit to socket outlet - IR was 2.91M ohms L-E, 184M ohms N-E and L-N, r1+r2 =0.32. there was evidence of the insulation breaking down behind a socket face - 2
Consumer units (2) not fastened to wall 2
Cooker hood feed in 2.5 mm T/E taken directly from cooker plate switch to a junction box, to hood. Not fused. (Radial to cooker protected by 30A bs 3036 fuse - 2
Downlighters in kitchen ceiling next to ceiling joists (as in 2/3 mm from the joists) and covered with insulation. (No signs yet of heat damage - only put in december 2010) - 2
The customer had the kitchen and bathroom refurbished Dec 2010. There are no certificates for the work (surprise, surprise having seen the work). The electric shower does not have RCD protection nor is there any bonding in the bathroom. The bathroom also has 2 downlighters fitted. The builder has re used some of the existing rubber insulated cables which look to be around 40-50 yrs old. Will try for some pictures later.
Thanks for any advice