Just thought i'd share some of last weeks experiences with you all.
Whilst carrying out a PIR on a 3 storey property last week I found there was no earth continuity at a metal fluorescent batten fitting on the top floor. One 1mm T&E so assumed feed was in the switch.
Removed switch on top floor (intermediate switching) Old Red, white & blue 3-core cable. There appeared to be an earth coming from the cable and terminating at the backbox. However a slight pull on this earth cable and one end came out of the 3-core cable.
Some idiot had used 3-core (no earth) and stuck a piece of 1mm earth cable inside the 3-core cable to magically earth the back box. Upon further inspection the other 2 switches where also wired like this. So no wonder there was no bleeding earth continuity at the light fitting!
Things like this really pee me off.
GS