Please bear with me here!
Can anyone offer some advice regarding the installation of downlights in a wooden ceiling.
A customer has had a bespoke summer house installed, I was tasked with providing the electrics which I attended to install today. On arrival it transpired that the summerhouse came pre wired. It is built at the factory, dismantled, transported to site then re assembled.
The installers were there today to complete the snagging list. They informed me it was all ready for test once I had connected, when I asked for the design and installation certificate they went very quiet.
Following some testing I found many many faults, not least of which on the lights.
No earth continuity from switch to fittings, Class 3 fittings with GU10 lampholders and halogen 50w lamps. Fittings butted right up next to the wooden ceiling joists and the ceiling itself is 10mm foil backed plywood with a skimmed and painted internal finish. 8 lights inside and 5 more outside in the eave. None are suitable for outdoor use.
I've told them and the customer the electrical design and install quality is carp. They informed me they did all of there own electrical work, design onwards. All without the aid of an electrician.
Indeed the big bloke who actually did the wiring asked "How come the lights are working if there is no earth then?" in a smug kind of way!!!
What I can't find in the BGB is a definitive statement concerning ceiling material and fire safety. Ceiling void depth is 70mm max, very little room for fittings to breathe.
I've informed them the current positions are a no no.
Manufacturer's instructions aside, would anyone allow the fitting of a downlight in a wooden ceiling?
Cheers.
Please bear with me here!
Can anyone offer some advice regarding the installation of downlights in a wooden ceiling.
A customer has had a bespoke summer house installed, I was tasked with providing the electrics which I attended to install today. On arrival it transpired that the summerhouse came pre wired. It is built at the factory, dismantled, transported to site then re assembled.
The installers were there today to complete the snagging list. They informed me it was all ready for test once I had connected, when I asked for the design and installation certificate they went very quiet.
Following some testing I found many many faults, not least of which on the lights.
No earth continuity from switch to fittings, Class 3 fittings with GU10 lampholders and halogen 50w lamps. Fittings butted right up next to the wooden ceiling joists and the ceiling itself is 10mm foil backed plywood with a skimmed and painted internal finish. 8 lights inside and 5 more outside in the eave. None are suitable for outdoor use.
I've told them and the customer the electrical design and install quality is carp. They informed me they did all of there own electrical work, design onwards. All without the aid of an electrician.
Indeed the big bloke who actually did the wiring asked "How come the lights are working if there is no earth then?" in a smug kind of way!!!
What I can't find in the BGB is a definitive statement concerning ceiling material and fire safety. Ceiling void depth is 70mm max, very little room for fittings to breathe.
I've informed them the current positions are a no no.
Manufacturer's instructions aside, would anyone allow the fitting of a downlight in a wooden ceiling?