I did a test the other day at a small block of flats with 2 storeys and 6 flats in each block. When i looked in the meter cupboard on the ground floor, i noticed that there was a 3 phase incomer feeding 6 mains fuses, but there was no neutral.
The neutral from the meter and the earth were connected together as expected for TNCS, but this then connected to a green/yellow cable strapped to the side of the incoming 3phase cable as a combined neutral/earth and not just earth as the colours suggest.
:|
Surely this is not right, but it is not part of my PIR as it is on the supply side.