hi there, i tested a ring circuit today and here are the values. r1 0.88 rn 0.87 r2 1.45 giving me R1+R2 value of 0.55
it was wired in 2.5 with 1.5 cpc , protected by a 32A rcbo type c, ze was 0.38 (tncs)
with this value it exceeds the value of 0.72 in table 41.3 but then according to table 41.5 the max earth fault loop for the bs en 61009-1 is 1667
would there be a problem with volt drop with these readings as i cannot determine the length of the circuit?Blushing
thanks guysBlushing
it was wired in 2.5 with 1.5 cpc , protected by a 32A rcbo type c, ze was 0.38 (tncs)
with this value it exceeds the value of 0.72 in table 41.3 but then according to table 41.5 the max earth fault loop for the bs en 61009-1 is 1667
would there be a problem with volt drop with these readings as i cannot determine the length of the circuit?Blushing