Customer is using a BG weatherproof socket outlet to charge his EV but he has noticed that it has caused burn marks on the socket faceplate.
Would it be possible to cut off the 3 pin plug on the EV lead and replace the socket outlet for a commando type, if so would you recommend 16A or 32A.
The installation for the socket outlet is as follows.
Sub main in the meter box with 10mm tails, 30ma rcd,16A mcb and the socket outlet is supplied with 2.5mm 3 core ho7 flex.
Thank you in advance Nigel.