r1 r2
tom1
Distinguished Member
Aug 7, 2009
2,330
on a loop in light circuit
is this done on switch or light fitting?
cheers andy
just r2 would be at switch then
r1+r2 would be at the furthest point with all two way switching closed to include the full circuit.
On a radial it is not a requirement to take a seperate reading for r2, but could be done, by the wander lead method.
At the switch you are only likely to have live, and an earth, so for all tests it may require the tests to be carried out at the light. However some testers do not require a neutral and such tests can be done at the switch.
its for my assesment, the lights are big (5 bulbs) so its a case of taking it down to get the r1 r2 and calculating zs,
Have you not got one of the adaptors they make life a lot easier when testing.
i can get one but do u still have to take it down to get to the earth,
can u use the metal fitting as the earth?? does not sound right
i can get one but do u still have to take it down to get to the earth, can u use the metal fitting as the earth?? does not sound right
As long as it is not class 2 that is what you are testing.
if using R2 method, then yes. after all, if its a class 1 fitting, then the metal must be earthed, so by testing to that, youre proving its earthed!
class 1 , so best way screw in the adaptor crock clip to light fitting itself and plug in to phase on the adaptor to get r1 r2, close switch to get reading and confim polarity,
this is same for zs but plug in the neutral as well, close switch
Just to tag along with this thread, when I did my testing on my extension lights it was before the fittings went up. (used conn blocks) I now have 10 GU10 spots up.
If the assesser asks me to do r1 + r2 on this circuit, will leaving the lamps in give me odd readings?
I know they will have to come out for IR tests.
Cheers
Bez
To be honest all types of lamps should be removed for all tests, which is why during installation tests are carried out during and final.
If you are doing a PIR then it may not be practicable to remove all lamps and this is when doing a ir test it is done with live and neutral connected and tested to earth.
You should not get any significant "odd readings" doing a r1+r2 test with lamps in situ, because the test is dead testing there should be no difference to the continuity of live or earth.