S soulman Senior Member Joined May 17, 2010 Messages 334 Reaction score 0 Nov 27, 2011 #1 hi, page 363 or brb radial circuit in 4mm, is that correct you can use a 2.5mm cable to supply 1 socket outlet as the protection device is 30a or 32a should this not be fused down. cheers
hi, page 363 or brb radial circuit in 4mm, is that correct you can use a 2.5mm cable to supply 1 socket outlet as the protection device is 30a or 32a should this not be fused down. cheers
Andy™ ©Resident Geordie™ Supporting Member Joined Jan 1, 2009 Messages 30,754 Reaction score 1,477 Location S. Tyneside Nov 27, 2011 #2 correct. no different to a spur in 2.5 from a ring at 32a
S soulman Senior Member Joined May 17, 2010 Messages 334 Reaction score 0 Nov 27, 2011 #3 Thanks andy of course it is, brain not working this morning cheers