I have an RCCB that trips off randomly. Sometimes it's two or three times a week and at other times it can go six weeks or more without tripping. It doesn't seem to be associated with switching any lights or appliances on or off and I'm worried it could trip off when we're away on holiday and we could lose all the freezer contents.
Does anybody know of an instrument I could hire or buy to find the fault that is causing this problem, please? I Googled "RCCB tripping randomly" and found your thread at
https://talk.electricianforum.co.uk/topic/32188-rccb-tripping-randomly/ . The person who started the thread, "Wah007" seems to have had some bad experiences with "cowboy" electricians so I'm a bit wary of calling anybody advertising in the local paper without some sort of recommendation. I do have a degree in Electrical Engineering and a MSc in Telecommunications Systems and I was a Fellow of the IEE before I retired in 2005, so I can understand technical explanations. However, I never trained as an electrician or took City and Guilds qualifications and I've never worked on domestic wiring, so I do need your advice. Can I find this problem and fix it myself, or do I need somebody with all the kit suggested to Wah007 by "Trailer Boy", and if so how do I find somebody who has the kit and knows how to use it? Thank you for any help you can offer.
There is NO instrument that can find a fault for you....
There are instruments that can:
a) measure the tripping times for an RCD.
b) measure the tripping current of and RCD.
c) measure the continuity of the circuit conductors.
d) measure the insulation resistance of the circuit cables.
e) measure the earth loop impedance at the supply and the furthest points on each circuit.
f) measure various portable and fixed appliance characteristics that are connected to your circuits.
etc..
ALL of which would probably be needed to assist diagnosing a possible cause....
BUT none of the above will be able solve anything without a person competent enough to know how to use them..
AND.. correctly interpret the results from them!
From what you say.. you have a poor design of installation with a single RCD protecting multiple circuits..
which also means there may not be a single cause..
It may be multiple problems across more than one circuit..
OR multiple sources of natural leakage.. that aren't actual faults at all!!
When was the installation wiring last tested?
The bottom line is...
The BS7671 specification for how your RCD should operate states...
It MUST operate when it detects a 30ma imbalance (leakage to earth).. (e.g. at 230v you are trying to find a path to earth of 7.6k or lower.. )
It MUST NOT operate if it detects a 15ma imbalance (leakage to earth).. (e.g. if RCD bit more sensitive at 230v you are trying to find a path to earth lower than 14.3k..)
You need to..
prove the operating characteristics of the RCD
prove the integrity of the circuits
prove the condition of connected appliances/accessories etc..
where about are you?