Hi there

I have to install two Sockets for some water steamers . i have 2 questions

1) i would you make them RCD due to water etc... is this right

2) if they are RCD protected sockets they will be connected to a timer to control on and off., so can some one tell me what type i need , i can only see Passice RCD's in the catolgue. would this be ok or would the RCD need reseting every time the power is off?

many thanks

 
I believe you can get active and passive so the active will be the ones you need. Maybe local wholesaler can advise?

 
"Active" RCDs are, I believe the type that trip when the power is cut, so if the timer is feeding the sockets (rather than fed from the sockets) you want passive RCDs.

 
No I is confussed as I thought it was the other way but I guess they are activly held closed by the power?

 
A quick check on MK's website confirms Active RCDs trip when power is cut/voltage drops far enough, passive RCDs don't.

 
Hi thereI have to install two Sockets for some water steamers . i have 2 questions

1) i would you make them RCD due to water etc... is this right
need a bit more info to answer that one properly, but generally I go for RCD if appliance involves water and people.

 
Consult the manufacturers instructions for a start. Is this in a commercial application?

 
Passive RCD's dont need re-set - the RCD's in your CU are passive

Active RCD's trip off at loss of power and need re-set - more used on RCD sockets/spurs & in line extension lead RCD's etc

 
Consult the manufacturers instructions for a start. Is this in a commercial application?
yes its commercial , its going in a bakery and they need some sockets for some steamers for bread! yumm yumm

 
You could use a suitabley IP rated industrial plug and socket. Some of these have RCD protection.

 
You could use a suitabley IP rated industrial plug and socket. Some of these have RCD protection.
So do non-industrial ones, e.g. BS1363 plugs and sockets.

 
So do non-industrial ones, e.g. BS1363 plugs and sockets.
The IP rating of that standard, would in my opinion not be adequate.

I would prefer to use sockets and plugs to BS ES 60309, and as there is water involved i would like them to also be to BS EN 60529: 1992.

 
The IP rating of that standard, would in my opinion not be adequate.I would prefer to use sockets and plugs to BS ES 60309, and as there is water involved i would like them to also be to BS EN 60529: 1992.
I missed the bit where it said they would get wet.

 