Hi All
I went to check out an RCD that was tripping out for no apparant reason. There was no clue to link it to any particular circuit. It was tripping about 6 times a day.
I checked the three ring mains, all tested ok I/R continuity. (I didn't have time to do any other circuits)
The Ze came in at 0.6ohms on a TNCS.
I also tested the RCD which stopped the auto test on 5x delta. 40ms. So I assumed the RCD could be faulty, so the next day changed it for a new one.
The lady said that since I'd checked it the day before, it hadn't tripped once.
After I put the new one in, I ran the tests again, it stopped on 5x delta again, since then this one hasn't tripped either.
This house and one across the road have got a bit of history, last year there were two neutral surges, the first blew the meters in both houses, the second blew a lot of the appliances in the second house but none in this. But since then his electric bill has shot up & British gas are saying he is using
I went to check out an RCD that was tripping out for no apparant reason. There was no clue to link it to any particular circuit. It was tripping about 6 times a day.
I checked the three ring mains, all tested ok I/R continuity. (I didn't have time to do any other circuits)
The Ze came in at 0.6ohms on a TNCS.
I also tested the RCD which stopped the auto test on 5x delta. 40ms. So I assumed the RCD could be faulty, so the next day changed it for a new one.
The lady said that since I'd checked it the day before, it hadn't tripped once.
After I put the new one in, I ran the tests again, it stopped on 5x delta again, since then this one hasn't tripped either.
This house and one across the road have got a bit of history, last year there were two neutral surges, the first blew the meters in both houses, the second blew a lot of the appliances in the second house but none in this. But since then his electric bill has shot up & British gas are saying he is using