Yes only sockets in the rcd, according to the owner. They have tried unplugging everything and still tripped, but then it reset and worked for a day or so. They say no d.i.y has been done.
Hello Jonathon,
Do the "faulty" rcd sockets include kitchen / utility sockets.
common cause I have found (On many occasions) are appliance that use water and incorporate heat.
i.e. water causes RCD to trip..
then heat drys out fault so resets and works OK again for a few days till faulty appliance in use again.
e.g. washing machines / dishwashers / electric kettles (cordless jobbies with separate base) / Steam Irons / coffee makers / smoothie makers etc..?
Also had fridge / freezer pumps that are on the way out.
and or kitchen appliances that have had visits from mice chewing around the back, exposed wires but not open circuit, just open enough for damp to occasionally trip.
Have you done the RCD 1/2 x1 & x 5 tests? (maybe also ramp test?)
have you checked the insulation resistance of the circuit?
both of the above would imply the circuit and RCD are OK.
YOU NEED TO DO THE ABOVE TESTS! to verify circuit!
Also an RCD thats been there for many years is probably proved itself to be OK? and IMHO its more likely to stick and NOT operate rather than operate at random?
Remember a loose or damage flex can cause intermittent faults?
my guess 80%+ more likely to be an appliance problem of some sort rather than fixed wiring or RCD? :|