even if the test button was wired on opposite sides' date=' there would be no difference.also, it WILL effect tripping in case of real fault. the 'fault' current can make its way back into neutral via the short in appliance, and go through RCD so less imbalance.[/quote']
Andy, WHAT exactly was unhelpful about my post #26
I was describing how, if it was wired the other way around, the TEST button would work even with the N-E fault.
With the N-E fault, as soon as any load is drawn of course the RCD would trip.
When I said "In any case, it will not affect it's tripping of a real fault, just the operation of the test button." I was refering to the polarity of the RCD, not the presence of the N-E fault, i.e irrespective of the polarity of the RCD, and imballance due to a real fault would still be detected and it would trip.
Of course, some manufacturers do state the polarity of their RCD, so you should stick to what they say, but many do not specify the polarity and can be wired wither way round, but a demonstrated the test button may not operate with a N-E fault when wired one way round.
If you are going to mark my post as unhelpful, I would really like to know what was unhelpful about it. I genuinely thought I was adding something to the explanation of why in some cases the test button does not work with a N-E fault.