- Feb 5, 2009
- 5,612
- 0
#SmartScreen
Level 3 Certificate in Electrotechnical Technology Unit 4 Sample questions answers
#Unit 4: Electrical maintenance: Inspection, testing and commissioning
Sample questions
Answer guide
1. List six methods of making an area safe before commencing work
Solution
use barriers and tapes
place warning signs in appropriate locations
Inform other workers in the area
isolate the supply
obtain a permit to work
shut down machinery in the area
(6 marks)
2. Describe the following types of maintenance:
a. preventative
b. corrective
Solution
a. Maintenance carried out to a schedule to try to prevent a breakdown of machinery during normal operation. (3 marks)
b. Corrective maintenance is work carried out when machines or equipment fails during operation and is not planned. (3 marks)
3. List six elements of a maintenance work plan
Solution
Definition of the task
Estimation of costs
Estimation of times taken
Safety procedures
Shut down arrangements
Permit to work
Access
Need for standby power supplies
(any 6) (6 marks)
4. Describe briefly:
a. a three-phase four-wire distribution system
b. the method of obtaining a single-phase supply from (a)
c. the importance of balancing loads on a three-phase system.
Solution
a. The three-phase four-wire system is taken from the secondary side of a
Delta-Star connected distribution transformer. The star point is connected to earth and neutral conductor. A four-wire supply provides choice of three-phase and Neutral, three-phase three-wire and single-phase supplies. Very rarely a
two-phase and neutral supply is used. (2 marks)
b. Single-phase loads are taken from the supply by connecting between any phase and neutral. (2 marks)
c. A balanced load will i) limit the neutral current, keep the cable size to a minimum as well as reducing to a minimum the switchgear sizes. (2 marks)
5. For a three-phase cage rotor induction motor describe the STAR-DELTA method of starting the motor.
Solution
The two ends of each phase are brought out to the starter. On starting, the windings are connected in star and when the motor reaches a set speed (often determined by a timer for automatic starting), the winding connections are re-made in delta for normal running. The main features of Star/Delta starting are
1. the start voltage is reduced to approximately 58% of its full load (run) value
2. the starting current is limited to between two and four times the full load current, rather than five to ten times for direct on-line starting
3. the motor torque is reduced during the starting
Sample questions
Answer guide
Solution
isolate the supply
(6 marks)
a. preventative
b. corrective
Solution
Solution
Estimation of costs
Safety procedures
Permit to work
Access
(any 6) (6 marks)
Solution
Solution