I've got a job to do which will entail reconnecting a consumer unit and final circuits back to the supply... about 3 months ago I disconnected it because the building had a roof leak in that area which wasn't found for a couple of months (if not more),,, the plaster board walls are also being ripped out where they have been affected by water... I have recommended that after the plasterboard has been removed that it allowed to dry throughly and anti fungicidal paint or whatever applied to the walls before anything else is done.
Now the existing supply to this CU (disconnected) is just DI 25mm tails... about 25m of them straight off henly blocks :redcard
So my question is how can I reconnect this..
DNO only allow 2 or 3 meters of exposed tails to CU's without additional protection
Burried cables <50mm require RCD protection (although this is a commercial building so it could come under instructed persons)
IMHO I would like to install this as a SWA submain with a switch fuse at the origin and a new DB (with RCBO protection) for the final circuits (if re-using the existing they will be throughly tested and inspected before replastering)
Now the existing supply to this CU (disconnected) is just DI 25mm tails... about 25m of them straight off henly blocks :redcard
So my question is how can I reconnect this..
DNO only allow 2 or 3 meters of exposed tails to CU's without additional protection
Burried cables <50mm require RCD protection (although this is a commercial building so it could come under instructed persons)
IMHO I would like to install this as a SWA submain with a switch fuse at the origin and a new DB (with RCBO protection) for the final circuits (if re-using the existing they will be throughly tested and inspected before replastering)