Well, not so much the formula, but the resistivity.
The resistance of a 2.5mm2 copper conductor of length 8m and resistivity p = 1.72 x 10-8 Ωm is: a) 0.055 Ω B) 0.55 Ω c) 0.12 Ω d) 5.56 Ω
I know the formula is R = pL/A (well, I believe it is). I just don't know how to work it out so I get the right answer. The part that's stumping me most is how do I interpret the p = 1.72 x 10-8 Ωm?
The answer I get is 0.000000054. It's safe to say I'm doing something completely wrong, I just can't seem to find out what it is.
Hi mate,
i worked it out to be 0.055
1.72 x 10-8 Ωm x 8 / 2.5 x 10-6
you use -6 as you are converting into metre's squared.
Hope this helps.
Stu
Hi mate,i worked it out to be 0.055
Hope this helps.
Stu
You wouldn't believe how much it helps, thanks a lot mate.
Hi Mfeely88,
just to clarify to help you understand a bit more
1 metre2=1000mm*1000mm= 10000000mm2
or
1mm2 = 1*10(to the power of-6)Metre2=0.000001M2
Just be aware that in some books it also might say resistivity of copper is either
1. 17.5 ohms *10-9
or
1.75ohms * 10-8
However these are both the same its just the decimal point is in a different place so dont get caught out.