Hi Andy, that is a great idea!! I will connect up a welder and get someone to have a weld and i will measure the voltage drop.
I had another idea i might try out later. The house is on "yellow" the same as the "faulty" line to the shed.
I get a much higher PSCC in the house [L2/N] than i do in the shed [more than double], which is a bit strange as they are both fed off the same LV main, and the shed service cable is much larger too. when i measure L1 - L3 1 get nearly 2KA if i go L1-L2 or L3-L2 i only get about 400 odd amps.
I will connect my meter to one phase in the shed [L1 or L3] and to L2 IN THE HOUSE!!! If then the PSCC rises to more like what i have measured between L1 + L3 then i know there is definitely something wrong with the L2 to the shed!!!!!
john..