I've been asked to add shaver sockets to a classy holiday let in two bathrooms. Wired to the 16th edition. Would like classy bright chrome fittings.
Thoughts - backed up by NAPIT inspector - insulated shaver socket - no problem - transformer isolated. Metal faced - into RCBO / supplementary territory. Bit dodgy However - suspect both fittings are to the same British Standard (but don't know for sure).
I've been thinking about the failure modes of a transformer. If the primary and secondary are isolated then by nature the Line and Neutral currents will be balanced. However if there is a short on the line side between primary and secondary - which would be feasible - then there would be no protection for the customer unless the circuit was on RCB.
Even if the circuit was RCB protected, If there was a fault on the appliance making the secondary live connect to the metal blades, the RCB would never trip as the currents are balanced with respect to the primary. Could this deliver a fatal shock with respect to earth?
Is it right to add a shaver socket without an RCB/RCBO upgrade - or is it right to add a shaver socket at all!
Any opinions?
Thoughts - backed up by NAPIT inspector - insulated shaver socket - no problem - transformer isolated. Metal faced - into RCBO / supplementary territory. Bit dodgy However - suspect both fittings are to the same British Standard (but don't know for sure).
I've been thinking about the failure modes of a transformer. If the primary and secondary are isolated then by nature the Line and Neutral currents will be balanced. However if there is a short on the line side between primary and secondary - which would be feasible - then there would be no protection for the customer unless the circuit was on RCB.
Even if the circuit was RCB protected, If there was a fault on the appliance making the secondary live connect to the metal blades, the RCB would never trip as the currents are balanced with respect to the primary. Could this deliver a fatal shock with respect to earth?
Is it right to add a shaver socket without an RCB/RCBO upgrade - or is it right to add a shaver socket at all!
Any opinions?