Just looked at a job, old shower not working, 10kw shower on a 6mm, 45 amp breaker , all connections burnt.
Ive told them they two options, replace shower for a lower power one or run a 10mm t+e in, they have gone for cheapest option of changing shower.
I aint fitted a shower now in years and when looking they all seem to be 8.5kw or above, can this go on a 6mm as by my working out 8.5kw comes to roughly 36 amp?
Shower has no RCD protection at present, am i ok to leave as is and straight swap or should i be rcd'ing the circuit?
Cheers in advance