Just looked at a job, old shower not working, 10kw shower on a 6mm, 45 amp breaker :eek: , all connections burnt.

Ive told them they two options, replace shower for a lower power one or run a 10mm t+e in, they have gone for cheapest option of changing shower.

I aint fitted a shower now in years and when looking they all seem to be 8.5kw or above, can this go on a 6mm as by my working out 8.5kw comes to roughly 36 amp?

Shower has no RCD protection at present, am i ok to leave as is and straight swap or should i be rcd'ing the circuit?

Cheers in advance

 
Hi D

Looking at the BRB - table4D5, depending on the the reference method, 6mm has a ccc ranging from 23.5A (in a stud wall with thermal insulation & cable not touching inner wall surface) to 47A (clipped direct).

Personally I would RCD that circuit - possibly RCBO???

 
Hi DLooking at the BRB - table4D5, depending on the the reference method, 6mm has a ccc ranging from 23.5A (in a stud wall with thermal insulation & cable not touching inner wall surface) to 47A (clipped direct).

Personally I would RCD that circuit - possibly RCBO???
very old crabtree board, would be a struggle to find rcbo to fit, got the wholesale on the job. Cable underfloors, then into trunking, through a studwall and into loft to pull switch

 
could use a seperate rcd

it could be argued that like for like swap,,,,no dangerous than before u started

 
could use a seperate rcdit could be argued that like for like swap,,,,no dangerous than before u started
but not installed to manufacturers instructions

easiest thing to do would be as theory says - RCD between MCB and shower. depending on length/installation method, you should easily be able to use an 8.5KW with 6mm

 
but not installed to manufacturers instructionseasiest thing to do would be as theory says - RCD between MCB and shower. depending on length/installation method, you should easily be able to use an 8.5KW with 6mm
 
compulsary on a shower, rcd protection even on a like for like swop.

 
in my post, prey tell under what circumstances would you not fit an rcd on a shower install . ??

 
in my post, prey tell under what circumstances would you not fit an rcd on a shower install . ??
Jl

i was refering to a straight swap of a like item

a new shower install i would rcd it

you dont have to rcd a ring cct when you change a socket

 
Just looked at a job, old shower not working, 10kw shower on a 6mm, 45 amp breaker :eek: , all connections burnt.Ive told them they two options, replace shower for a lower power one or run a 10mm t+e in, they have gone for cheapest option of changing shower.

I aint fitted a shower now in years and when looking they all seem to be 8.5kw or above, can this go on a 6mm as by my working out 8.5kw comes to roughly 36 amp?

Shower has no RCD protection at present, am i ok to leave as is and straight swap or should i be rcd'ing the circuit?

Cheers in advance
9500w @ 230v = 41A

6.0mm clipped direct or in masonry (method C), with no major insulation issues can carry 46A

May need to check length of run for volt drop.

If its an old property probably not buried in truck loads of insulation,

so stick 40A MCB & up to 9.5K as per loads of properties which are working perfectly well.

I would most likely go 9.0k or 9.5k (If you read the small print, the 9.5k rating on the box is normally @ 240v NOT 230v)

AND I would stick a standalone RCD on the circuit, (allow

 
when would you not fit an rcd on a shower ??? i honestly dont know. ??

 
when would you not fit an rcd on a shower ??? i honestly dont know. ??
regs do not require it. only needs fitted to protect cable (if req'd), or if the manufacturers instructions say it must be RCD'd

i still make sure there is always an RCD for showers though, even if its not required

 
req for rcd, All circuits in a bath or shower room.(cant find a reg )

i cant find anywere an option for not fitting 1 on a shower. ??

 
req for rcd, All circuits in a bath or shower room.(cant find a reg )i cant find anywere an option for not fitting 1 on a shower. ??
depends on shower. i have seen some where shower is outside the room, and pipe feeds into bathroom. this would not require RCD (but if controls are electronic from inside, then it would)

under 16th, RCD covering all of bathroom wasnt required

 