Smoke alarm off lighting circuit

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

meady

Senior Member
Joined
Jun 19, 2009
Messages
197
Reaction score
0
Just a quick one, can you install a smoke alarm of the lighting circuit if there is no rcd? The lighting circuit doesent go into a bathroom so I'm asuming I can work on it without adding the rcd

thanks for any advice

 
Well, if your additions are not in the walls <50mm then I suppose you could!Lets see what the others have to say :D
+1

new builds normally own circuit

 
Think we discussed this in length a while back.

If you put them on the lighting circuit, they must have a seperate means of isolation.

Will try and dig up the thread unless Patch beats me to it.

 
Part B of the building regs states a requirement for a seperate cct from the distribution board,,,this is for new builds.

old builds,,, lighting cct acceptable

 
Part B of the building regs states a requirement for a seperate cct from the distribution board,,,this is for new builds.old builds,,, lighting cct acceptable
Erm does it. This is from AD B

15.5 Recommendations for power supplies for Grade D systems

The following recommendations are applicable.

a) The normal supply for smoke alarms and any heat alarms in a Grade D system should be derived from

the public electricity supply to the dwelling. The mains supply to the smoke alarms and heat alarms

should take the form of either:

i) an independent circuit at the dwelling

 
Erm does it. This is from AD B15.5 Recommendations for power supplies for Grade D systems

The following recommendations are applicable.

a) The normal supply for smoke alarms and any heat alarms in a Grade D system should be derived from

the public electricity supply to the dwelling. The mains supply to the smoke alarms and heat alarms

should take the form of either:

i) an independent circuit at the dwelling
 
I think this is the thread you're thinking of:

http://www.talk.electricianforum.co.uk/showthread.php?t=7776&page=2

The upshot was that smoke alarms can be on their own circuit or combined with a lights circuit. Either way, the smokes must be provided with a means of isolating them from the supply without interupting the lights.

Many ways to skin a cat and all that: I'm putting in the wiring for a loft conversion at the moment. This entails adding smoke alarms (x3). I'm extending the upstairs lights to give lighting for the new rooms and adding the smokes to this circuit. The smokes will take their supply from the 2nd floor landing switch, so to achieve the requirements above, I'm putting in a grid switch with one switch and one key switch for isolating the smokes (and a label on the CU).

If you can take the smokes supply back to the CU then a means of isolating could be to simply remove the supply cable from the MCB (label the cable for easy ID).

 
As for whether you need to add an RCD, well the usual rules about buried cables and special locations apply as normal, so you need to decide if your new work falls under these requirements.

 