Did a job for an old dear on Monday . Storage heater Creda 2.3KW about 10 yrs old she says " Only half of it gets hot I need a new one"

So open it up , can't see anything blown .

All three elements the same resistance .

Frig the time switch and read current , 9.3A

All elements have 240V applied .

Input stat calling for heat .

All 3 elements getting hot .

So I pronounce it alive & well , tell me if it hasn't heated up over night .

She phones today to say its hot at the top and cold at the bottom , which I noticed when I tripped it on for an hour .

Any ideas , all the others get hot all over so she still thinks she needs a new one, but if it pulls the correct current it has to be working !! . Or am I missing something ?? My only thought is that the output flap was open slightly , set at 4 . May phone her tomorrow to suggest closing the output flap.

 
Last edited by a moderator:
Did you take the inner cover off to access the elements, or just test from the terminals?

I'm just thinking there may be something wrong with the bricks/casing if you're getting the right input but the wring output.

 
Last edited by a moderator:
Thermostat set too low? I find a HUGE variation in heat input vs settings i.e same setting on 2 heaters gives different results.

Boost flap stuck open, or boost control set too high. With the flap open it will act more like a convector with heat coming straight out, and less heat will go into the bricks.

Also it's only been on 1 night. May not be enough to fully charge it?

 