PaulThe change from the 14th to the 15th Edition of the IEE Wiring Regulations in 1981 created a big upheaval in the electrical installation industry as many new concepts were introduced and many existing practices were expanded or enhanced - one of those being supplementary equipotential bonding. To a great extent, the 15th Edition was based on CENELEC harmonised documents (HDs) (more so now with the introduction of the 17th Edition).
I knew this as I now have both the '76 version of the 14th & the 81 version of the 15th.
I recognised the similarity in the 15th to the subsequent regs.
I don't have a copy of the CENELEC doc of the era unfortunately.
HD 384.4.41 was the basis for Chapter 41 of the 15th Edition - Protection against electric shock, which had requirements for supplementary equipotential bonding in Regulation 413-7, reproduced here:
413-7 Within the zone formed by the main equipotential bonding, local supplementary equipotential bonding connections shall be made to metal parts, to maintain the equipotential zone, where those parts -
(i) are extraneous conductive parts, and
(ii) are simultaneously accessible with exposed conductive parts or other extraneous conductive parts, and
(iii) are not electrically connected to the main equipotential bonding by permanent and reliable metal-to-metal joints of negligible impedance. NOTE - Where local equipotential bonding is provided in accordance with Regulation 413-7, metalwork which may be required to be bonded includes baths and exposed metal pipes, sinks, taps, tanks, and radiators and, where practicable, accessible structural metalwork
This is the reg no. I was looking for.
I had found 471-22 for the special provisions and exceptions, but had not yet found this reg group.
Thank you.
Those far reaching changes, issued on 31st March 1981, are still being felt today with designers and specifiers still implementing the requirements for supplementary equipotential bonding from the 15th Edition. Much of the confusion can be attributed to the note of Regulation 413-7 which required the bonding of all metallic items, essentially, those within the designated equipotential zone. This led to the installation of supplementary equipotential bonding of general metallic items such as baths, ceiling grids, hand rails, kitchen sinks, radiators, pipework at boilers, etc. Thankfully, we have moved on from this general concept.
Thus, IMHO it is still the ambiguity that required all this bonding!
We were on the start of the slippery slope.
I had the language differences explained to me once, but I can't remember it, the thing that does stick is something like the difference between Anglo-Saxon & Romanic or something, I'll rack my brains and try to find out what was discussed!
HTH