Was asked a while ago to look (just a quick look) at property that was being bought by some one i had done work for before. he wanted old fuse board changingView attachment 665
to 17th CU. i asked him to get an isolator fitted and also for them to check earth and give me some where to connect to as it was looped for next doors too, any way isolator fitted and earth checked (apparently).this is my first incounter with a TNS so after some advice, is the earth adequate? (i dont think it is) should them clamps be used for TNS earth? and should it be me to change or DNO.
View attachment 666
View attachment 667
View attachment 668
View attachment 669
View attachment 670
Ze was 0.12ohms
any advice most apprieciated
cheers Wayne
to 17th CU. i asked him to get an isolator fitted and also for them to check earth and give me some where to connect to as it was looped for next doors too, any way isolator fitted and earth checked (apparently).this is my first incounter with a TNS so after some advice, is the earth adequate? (i dont think it is) should them clamps be used for TNS earth? and should it be me to change or DNO.