good evening,

I have to run a feed to a shed on a TT installation.The cable is clipped then buried.

I have 2 questions.

1- I'm using a henley block to feed the supply. do I need to RCD the cable at source and then just mcbs in the shed ?.

2- Can I use 2 core and add rod at the shed?.

Cheers.

 
1, Depending on the Ra you would need to RCD to get your disconnection times down to 2 secs (am I right on the time for distribution circuit??)

You will need to fit a fused isolator or something rather than just splitting the tails.

2, I sometimes use the armouring as the earth for the cable so 2 core works for me (although it tends to be PME or TNS so I pop a rod in for the shed)

 
1, Depending on the Ra you would need to RCD to get your disconnection times down to 2 secs (am I right on the time for distribution circuit??)You will need to fit a fused isolator or something rather than just splitting the tails.

2, I sometimes use the armouring as the earth for the cable so 2 core works for me (although it tends to be PME or TNS so I pop a rod in for the shed)
I'm obviously using a breaker from the henley block.My question is since the shed sockets and light are rcd protected.Do I need to rcd the swa at source or not?

 
Because the armouring is earthed it only requires an RCD if the earth fault loop is too high to get the required disconnection time, which being a TT supply is likely

 
ALL cables in a TT installation require RCD protection for fire protection and 30mA for shock protection,, so it needs RCD protection at the source.

You could have a 100mA 'S' type at the source and then 30mA for the final circuits

 
Although your right that TT needs RCD in most cases I don't think its an actual regulation,

It depends on the earth being decent and reliable

Disconnection needs to be 0.4 secs on TT distribution

 
i dont think its a reg but just near enough unachivable without an rcd

 
Very unlikely loop will be low enough without an RCD on TT system to comply so RCD will be needed and would you really want to risk putting a circuit on TT system without an RCD remember its your name on the certificate if it goes wrong.

 