Taking Zs At Light Switch

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.
Status
Not open for further replies.

r.b

Well-known member
Joined
Feb 8, 2011
Messages
379
Reaction score
0
I have a metrel mi 3100 im going round doing the repairs that a tester has found one is high zs at light switch mines a 3 probe line ,neutral and earth Im ok with sockets ,pendants,how do I test zs at a switch with line and earth there?Or cant I?I have thought about clipping earth and neutral probes together and putting this on earth and brown probe on line will this take the reading like that?

 
Problems I can see if circuit is RCD protected its possible the Rcd will go before the test is done. Also is your meter capable of doing this test?

 
how do i get the high reading down ?put a new switch on sometimes lowers it

 
high readings are generally caused by poor connections, could be at the switch or further down the circuit - testing will reveal!! tweak something, test again, keep tweaking things until reading changes, then you know you have found the issue (might be more than one)

 
yes this is what the guy probly used a just ad a go of mine joining earth and neutral together it dnt work tripped a dual rcd board on a zs rcd setting

thing is all i can do is test at lights!Al tighten up switches

 
A tested a switch tonight at my house just trying it,the houses on where I am testing are no rcd

 
what so it works piggy backing on no rcd

 
Slips my Metrel had a banana socket on the back of the earth clip for that purpose, and it showed it in the instructions, so who knows, mind you Metrel is Polish or Russian or something.

 
I would go to the pendant and test the lighting feed and then test the switched live side with switch closed. If that showed high reading on the switched live  i would then check out the switch and pendant.

 
the reading was over 200 ohms the zs at light switch 

 
how to do a 3wire test at a light switch,

turn switch off

ensure a normal filament lamp is in situ

Line probe to line at switch

earth probe to earth

neutral probe to switch wire at switch

test,


:D