How would you test a circuit with fixed low energy light pendants for insulation resistance

L -N to E or 250v.

 
Exactly the same as any circuit with equipment vulnerable to testing.

But....

You knew that anyway didn't you...

I can tell from your initial suggestion...

If ever any doubt.. you can always check On-Site-Guide recomendation...

Which you will of course also be saying...

"Oh yes SL you mean I should read page 83"

10.3.3 Insulation Resistance

i Pre-test checks

b if circuit includes sensitive devices..... etc blah blah

2 a measurement should be made between the live conductors (Line & Neutral) connected together and the protective earth only.

and I would say..

yep spot on Harvey good of you to mention that cuz it always helps those learning the trade to have a reference to check back to!

:Salute

NOW

beer time!

GuinnessGuinnessGuinnessGuinness

 
I always test at 250v first to make sure it's clear before putting 500v down it. May be unnecessary but don't wanna break anything sensitive. Cheers

 
Had an odd one today on a PIR, Could not disconnect an extension lead with Neon from a bedroom socket as a Water bed was tight up to it!

Tried a L+N to Earth at 250 Volts got >9.99 M ohms, so went for 500 Volt test and got 0.33 M ohms

Any one got any ideas?

 
Had an odd one today on a PIR, Could not disconnect an extension lead with Neon from a bedroom socket as a Water bed was tight up to it!Tried a L+N to Earth at 250 Volts got >9.99 M ohms, so went for 500 Volt test and got 0.33 M ohms

Any one got any ideas?
Did it have surge protection? Every time I've tested a property with surge protection extension leads they always show 0.3meg to earth!

 
Had an odd one today on a PIR, Could not disconnect an extension lead with Neon from a bedroom socket as a Water bed was tight up to it!Tried a L+N to Earth at 250 Volts got >9.99 M ohms, so went for 500 Volt test and got 0.33 M ohms

Any one got any ideas?
Cut the extension lead wire then rewire it after? That's what I did when I had one going to a socket behind a bookcase that would take a week to move

 
Did it have surge protection? Every time I've tested a property with surge protection extension leads they always show 0.3meg to earth!
Quite...

Capacitance in surge protection circuitry..

causing variation of continuity..

:)

 
Could be inductive parts in the filter which would offer back emf/increasing impedance to restrict rapid increases in a.c. voltage, aka surges, but offers little impedance to the d.c. chucked out by our testers?

Once above the 230/240 V threshold then perhaps there is a "zener" type device that kicks in?

Never studied them to be honest, always just bought filters spec'd by the filter maker, or spec'd them from our software when I used them a lot!

 