Disconnect the bonding from the MET, crock clip it, then test on pipe immediately next to clamp - this proves integrity of the clamp connection as well.yeah i know how to do the test but specifically wanted to know if you disconnected the cable at the bonding point and tested that, as PC pointed out doing the test to the pipe or clamp with the cable connected doesn't actually confirm the main bonding cable as a low reading could be shown from the pipe being earthed by other means.
now thats an answer Applaud SmileyDisconnect the bonding from the MET, crock clip it, then test on pipe immediately next to clamp - this proves integrity of the clamp connection as well.Doesn't matter if the pipe goes to earth then, as you're not testing to earth, you're only testing the resistance of the bonding
QUE?????Just remember to null your meter properly before testing and un-null afterwards to prevent confusion in any other testing.
I suspect he means re-null the leads without the wander lead in the circuit!QUE?????Un-null??
Ah! Penny`s just dropped. As in, remove the resistance of the wander lead from the nulled value. Sorry. Just looked at post and thought "summat wrong here, my tester doesn`t HAVE an `un-null`!"
:coat
very well put,Disconnect the bonding from the MET, crock clip it, then test on pipe immediately next to clamp - this proves integrity of the clamp connection as well.Doesn't matter if the pipe goes to earth then, as you're not testing to earth, you're only testing the resistance of the bonding