If you have an RCBO on a shower circuit and was doing the rcd test. Would you connect the meter L/L N/N on rcbo and Earth to Earth Bar in CU or would you do test with meter connected at shower end. Thanks

 
RCD testing should be done as close to the origin of the circuit as possible
Concur!

At the CU. Direct onto the RCBO. Page 91 point 11.1 OSG!

RCBO's are classed as the generic type name RCD in this context..

see first two lines top of page 91! ;)

 
considering the probes usually need help in place, its easier to do it at the board and re-set with other hand, than constantly moving between locations

 