2 lighting circuits, 2 RCBOs. Checked for the borrowed neutral, insulation resistance between neutral of each circuit and proved OK. So though to myself, grand job, crack on with the rest of the tests, connect up, paperwork, then off to the pub for a couple and watch the footie.
However, when testing insulation resistance between L-N, L-E and N-E, I get a dead short 0Mohms on both circuits. I don't understand, surely a dead short would have been an issue a long time before on the old fuse board, which was a BS3036 jobbie.
What stumped me though was if both circuits are put into just 1 RCBO, it resets and if they are put into their own RCBOs, either one will not reset. Why is this, especially if i'm seeing a dead short whilst insualation testing?
However, when testing insulation resistance between L-N, L-E and N-E, I get a dead short 0Mohms on both circuits. I don't understand, surely a dead short would have been an issue a long time before on the old fuse board, which was a BS3036 jobbie.
What stumped me though was if both circuits are put into just 1 RCBO, it resets and if they are put into their own RCBOs, either one will not reset. Why is this, especially if i'm seeing a dead short whilst insualation testing?