Went yesterday to do a cooker swap. 6mm cable coming from outlet. Cooker switch above with integral socket outlet, with a washing machine plugged in. 9KW cooker, old and new same rating. 32A MCB. I had already upgraded the bonding at a previous visit. Seemed simple.
Looked in Cooker switch and saw 2x2.5mm cables feeding it, with 6mm t&e out. There was a loose(ish) 2.5mm neutral, it fell out when I was moving the faceplate.
Looked in CU 2x2.5mm wires in the cooker mcb
Disconnected the circuit.
So Today I ran 6mm all around the kitchen to a new one gang switch and used one of the legs of the 2.5mm cable as an unfused spur, from a socket circuit in the CU, for a double socket above the freestanding washing machine.
I can only think that the "sparkies" who installed the CU weren't given any 6mm cable, so improvised.
Also it was a split load (plastic) CU with an RCD main switch and a second RCD. They obviously did not know how to wire 2 RCDs so connected everything to the main switch RCD, leaving the second one at the far left.
I am going to recommend tests on the other circuits, just in case. Client is the Church, God bless em.
I was going to do a "spot the fault" thread, but the pic quality is v poor.
Looked in Cooker switch and saw 2x2.5mm cables feeding it, with 6mm t&e out. There was a loose(ish) 2.5mm neutral, it fell out when I was moving the faceplate.
Looked in CU 2x2.5mm wires in the cooker mcb
Disconnected the circuit.
So Today I ran 6mm all around the kitchen to a new one gang switch and used one of the legs of the 2.5mm cable as an unfused spur, from a socket circuit in the CU, for a double socket above the freestanding washing machine.
I can only think that the "sparkies" who installed the CU weren't given any 6mm cable, so improvised.
Also it was a split load (plastic) CU with an RCD main switch and a second RCD. They obviously did not know how to wire 2 RCDs so connected everything to the main switch RCD, leaving the second one at the far left.
I am going to recommend tests on the other circuits, just in case. Client is the Church, God bless em.
I was going to do a "spot the fault" thread, but the pic quality is v poor.