hi all
i have been asked the question ( below ) and cant find the formula anywhere any help would be greatly appreciated.
a transformer has a rated power of 24kva and a power factor of 0.95 and the losses are 1400 watts
calculate the overall efficency.
so how would it be if
a transformer has a rated power of 1kva and a power factor of 0.75 and the losses are 100watts
so how would it be ifa transformer has a rated power of 1kva and a power factor of 0.75 and the losses are 100watts
use my working above and change values for your new question - do this and someone will tell you if you got it right
you are a absolute star many thanks for your help
Hi capemoff...
welcome to the forum mate:DGuiness DrinkGuiness DrinkGuiness Drink
as you have found out....
there's good help on ere!!!:)Applaud Smiley
so doe be afraid to come back and ask more!!! ;)
tried working this out from andyc answer above but getting no where the 600W is throwing me could somebody please show me how to work this question out.
a transformer has an output of 12kva & a power factor of 0.9 the total losses in the transformer are 600w = what is the efficiency of the transformer = 94.4% answer
done the 12x0.9 = 10.8 this is where i get lost off with the 600w
thanks for looking.
output/(output+losses)x100 = Transformer Efficiency.
Closest answer i got was 94.73%
with (12000 x 0.9)/((12000 x 0.9)+600)x100
tried working this out from andyc answer above but getting no where the 600W is throwing me could somebody please show me how to work this question out.a transformer has an output of 12kva & a power factor of 0.9 the total losses in the transformer are 600w = what is the efficiency of the transformer = 94.4% answer
thanks for looking.
i first did the same calculation as yourself then re read the question :z :z
12kva output has to be transposed to kw to calculate 600w loss. i think. Guiness Drink