Basic question.... "TT Am I missing something Stupid"?
Been to look at an installation today .....
Previous customer moved house... to a more rural location wanting a few jobs done....
Main House TT.. with remote garage approx 20m physical.. maybe 25m+ cable run (6.0mm 3core SWA, Red/Yellow/Blue) between buildings...
Garage CU working Sockets, Light plus onward to garden summer house and driveway gates.
Zbd @ garage 47.4 ohms Off a 32A 60898 MCB at main house..
NO RCD protection on Sub-main from House to garage...
Garage is getting earth from main house rod...
Had this of been a TNS / TNCS at the house, I would have probably TT'd the garage anyway..!
But... Working mostly in an urban part of Midlands, I only get to see maybe two or three TT's every 4or5 years, so not 100% hot on historic requirements..
My gut feeling is that the garage should have had its own rod independent of the House..
Plus the sub-main feeding the garage should have been RCD protected to meet sub-main disconnection times...???
Looks like the kitchen was refurbished more recently Blue/Brown ring final..
I am thinking that Captain Kitchen Fitter replaced the CU during this kitchen refurb, with little or no knowledge of earthing arrangements?
Was this arrangement actually acceptable pre the Harmonised colours??
Thoughts please gents??????????????????
Been to look at an installation today .....
Previous customer moved house... to a more rural location wanting a few jobs done....
Main House TT.. with remote garage approx 20m physical.. maybe 25m+ cable run (6.0mm 3core SWA, Red/Yellow/Blue) between buildings...
Garage CU working Sockets, Light plus onward to garden summer house and driveway gates.
Zbd @ garage 47.4 ohms Off a 32A 60898 MCB at main house..
NO RCD protection on Sub-main from House to garage...
Garage is getting earth from main house rod...
Had this of been a TNS / TNCS at the house, I would have probably TT'd the garage anyway..!
But... Working mostly in an urban part of Midlands, I only get to see maybe two or three TT's every 4or5 years, so not 100% hot on historic requirements..
My gut feeling is that the garage should have had its own rod independent of the House..
Plus the sub-main feeding the garage should have been RCD protected to meet sub-main disconnection times...???
Looks like the kitchen was refurbished more recently Blue/Brown ring final..
I am thinking that Captain Kitchen Fitter replaced the CU during this kitchen refurb, with little or no knowledge of earthing arrangements?
Was this arrangement actually acceptable pre the Harmonised colours??
Thoughts please gents??????????????????