I`m going to stick my oar in here. I`d make certain that there is nothing else connected into that cable, or the rod. 6.69 ohms Ra is MUCH lower than I`d be comfortable with.
Where you are asked for max Ze, insert Ra on a TT system. 30-90 ohms typical. <10 suggests either:
1. an amazingly good rod
2. a parallel path, as suggested above.
Max Zs for mcb`s has no bearing on a TT system, as they are seriously unlikely to trip due to earth fault. If your meter shows PFC when doing EFLI tests, you`ll see very low readings, in the order of a few amps. This is why an RCD is required, as an earth fault could well go undetected by the protective device!