Hi, grateful for any thoughts..my brain is slowing..
scenario = House with TT..doing EICR before possible major updates. (To give you an idea of the condition the house does not even have RCD fault protection, and what was acting as a Voltage ELCB has been at some point disconnected from any earthing route and is now simply acting as an isolation switch!) I digress..
Got an Ra of around 80ohms..condition of rod (if it is even a rod...unknown for now as it looks as if its now lies under an extension.) Main Bonding to Gas, but none to Water that I can yet find. Example of a Zs on the Ring Main was 2.2ohms (BS 3871 type 1) obviously too big but fine for a TT IF they had RCD. Being a newbie to TT systems I thought I'd try a Z's with the gas bonding disconnected..result >80ohms. This was the same on all circuits.
Main bonding naturally provides some parallel earth in any system, but this difference would suggest to me that in the event of a fault current wanting to find the least resistance to earth that any earth fault in the house would always go down the Gas bonding?..surely effectively making the gas supply the main earthing?.Ie a no no!
I guess it must be the same on all TT systems that have an Ra above a few ohms?. but any thoughts would be most.. :Welcome:
scenario = House with TT..doing EICR before possible major updates. (To give you an idea of the condition the house does not even have RCD fault protection, and what was acting as a Voltage ELCB has been at some point disconnected from any earthing route and is now simply acting as an isolation switch!) I digress..
Got an Ra of around 80ohms..condition of rod (if it is even a rod...unknown for now as it looks as if its now lies under an extension.) Main Bonding to Gas, but none to Water that I can yet find. Example of a Zs on the Ring Main was 2.2ohms (BS 3871 type 1) obviously too big but fine for a TT IF they had RCD. Being a newbie to TT systems I thought I'd try a Z's with the gas bonding disconnected..result >80ohms. This was the same on all circuits.
Main bonding naturally provides some parallel earth in any system, but this difference would suggest to me that in the event of a fault current wanting to find the least resistance to earth that any earth fault in the house would always go down the Gas bonding?..surely effectively making the gas supply the main earthing?.Ie a no no!
I guess it must be the same on all TT systems that have an Ra above a few ohms?. but any thoughts would be most.. :Welcome: