Hello all
I was asked to quote for a couple of new security PIR type lights in a new house recently.
The house is about five weeks old and has a Contactum consumer unit. There are four ring circuits protected by one 30ma RCD the rest of the circuits are protected only by MCBs.
My query concerns the identification of the power company earthing scheme.
The consumer unit is neatly built in to a floor to ceiling cupboard. The is a boxed section made out of plywood above the CU containing the cables. The cables then disappear into the ceiling void.
Thus my usual clues as to the earthing type like seeing an incoming cable from the power company with an earth clamp on it are not available to me. There is no PME label anywhere to be seen.
The house is part of a small modern cul de sac in an urban development on the edge of a town and there are no visible overhead power cables running to the houses.
The lady owner is particularly worried about any electrical work damaging her brand new property so taking a crowbar to the plywood boxed section above the consumer unit is not an option.
There is no sign of an earth rod anywhere outside the house.
I took a Zs reading from one of the sockets on the kitchen ring and got a reading of 0.37 ohms.
I can
I was asked to quote for a couple of new security PIR type lights in a new house recently.
The house is about five weeks old and has a Contactum consumer unit. There are four ring circuits protected by one 30ma RCD the rest of the circuits are protected only by MCBs.
My query concerns the identification of the power company earthing scheme.
The consumer unit is neatly built in to a floor to ceiling cupboard. The is a boxed section made out of plywood above the CU containing the cables. The cables then disappear into the ceiling void.
Thus my usual clues as to the earthing type like seeing an incoming cable from the power company with an earth clamp on it are not available to me. There is no PME label anywhere to be seen.
The house is part of a small modern cul de sac in an urban development on the edge of a town and there are no visible overhead power cables running to the houses.
The lady owner is particularly worried about any electrical work damaging her brand new property so taking a crowbar to the plywood boxed section above the consumer unit is not an option.
There is no sign of an earth rod anywhere outside the house.
I took a Zs reading from one of the sockets on the kitchen ring and got a reading of 0.37 ohms.
I can