Hello all,
Been and done a visual inspection for a landlord this evening. Found a couple of problems and wanted to check I've got the coding right. I've put the fault and codeing below. Also could do with some help with a BS number. The fuses were the pop out type made by wylex and are in a metal clad box.
Gas bonding only 6mm - code 2
Water bonding not visible - code 1
Main earth to fuse box 6mm - code 2
Front fuse cover missing from fusebox - code 1 (small fingers could touch live parts)
Kitchen lighting 2 way switching causing 1 light to flash as switch is changed over probably a strapper problem - code 3
Oven cable from oven switch in 2.5mm T+E - code 1 (its on a 30A fuse, could see it as kitchen being refurbed and cooker not connected)
No RCD - Code 4
No supplimentary bonding in bathroom - Code 3
No supplimentary bonding at boiler - code 3
Also several of the socket covers in the kitchen have had the screws removed and are hanging off as its all being retiled - do I need to put this down as they are all going to be refitted properly once the tiles have dried?
Been and done a visual inspection for a landlord this evening. Found a couple of problems and wanted to check I've got the coding right. I've put the fault and codeing below. Also could do with some help with a BS number. The fuses were the pop out type made by wylex and are in a metal clad box.
Gas bonding only 6mm - code 2
Water bonding not visible - code 1
Main earth to fuse box 6mm - code 2
Front fuse cover missing from fusebox - code 1 (small fingers could touch live parts)
Kitchen lighting 2 way switching causing 1 light to flash as switch is changed over probably a strapper problem - code 3
Oven cable from oven switch in 2.5mm T+E - code 1 (its on a 30A fuse, could see it as kitchen being refurbed and cooker not connected)
No RCD - Code 4
No supplimentary bonding in bathroom - Code 3
No supplimentary bonding at boiler - code 3
Also several of the socket covers in the kitchen have had the screws removed and are hanging off as its all being retiled - do I need to put this down as they are all going to be refitted properly once the tiles have dried?