Page 44 OSG Table7.1 gives cable size, and max length for different protective devices and types of circuits. Useful book if you don't already have it.
Greetings folks
can some one tell me what all the abbreviations mean??
mv = milli Volts
A=area m = metre
1000 = ?
P
Can anyone enlighten me on how to work out Volt Drop on a ring circuit?
Hello Trip! :)
we know max Volt drop = 3% lights 5% other circuits!
so 11.5v for socket circuits..
Lets chuck a few numbers around..
First.. lets consider a radial circuit
20amps
2.5mm
30 meters long
from OSG pg 133 table 6E2:- 2.5mm, volt drop = 18mz/amp/meter
Assume circuit running full wack!
so volt drop = (18mv * 20 * 30)/1000 = 10.8v ok! :)
Now lets assume two identical radial crvuits...
joined together at furthest point.... is a 60m ring circuit,
but cuz two parallel identical paths, Resistance is halved
& volt drop halved...
i.e would be equivalent to 18x20x15/1000 = 5.4v
or ( 18x20x60/1000 ) /2 = 5.4v
but remember its a bit more tricky with an existing ring circuit with branches and spurs of;)f!
does it make any difference if its armoured cable
also is there a specific place in the OSG in relation to armoured or is it irrelavant when working out volt drop.
I have just bought the OSG and am still getting to grips with it but cannot seem to find any specific info on armoured cable
cheers
p
does it make any difference if its armoured cable also is there a specific place in the OSG in relation to armoured or is it irrelavant when working out volt drop.
cheers
p
the volt drop is different, check the tables in 7671. the rest of the formula is the same
thanks for that
will have to wait till im back to college for that
have not taken the plunge on the that baby yet
regards
P