That will be the 'skin effect' if I remember from my college days many many years ago in a land far away.Further to my post above, just spoke with bg nexus tech. They say that it is not necessarily the CSA which is important but more the surface area of the outside surface, as electrons prefer to travel along the surface of a conductor, one of the reasons why stranded wires can carry more current, the csa might be the same but the surface area is much higher. In this case the csa of the steel is 6mm sq but the surface is 14mm. By comparison a 6mm sq copper cable has a circumference of 8.7mm.
I know that the required csa calculated by the adiabatic equation would normally be less than the actual csa of the cpc.
But I still think that there is not much wiggle room in the design. BG nexus seem happy with it though and have not had any problems in the 12 years they have been making them.
That will be the 'skin effect' if I remember from my college days many many years ago in a land far away.
However I would be in the same camp as you Rich in thinking that earth is not man enough.
The skin effect is an phenomena that applies to RF frequencies of many MHz and above. It is not relevant to 50Hz mains.
At 60 Hz in copper, the skin depth is about 8.5 mm. At high frequencies the skin depth becomes much smaller
From https://en.wikipedia.org/wiki/Skin_effect
I really don't think the skin effect has any relevance to domestic or even industrial 50Hz mains unless you are dealing with cables more than 17mm diameter.