Thinking about installing a Wisebox for garden fountains and LED circuits. Looking to take a 2.5mm 3core swa out to box but unsure if there is room to terminate gland into box. Also note that 4 x 10A cartridge circuits inside. Where do we stand on fusing down the circuits if the pumps and single light circuits are only 1mm pvc/pvc?

Anyone any experience?

 
i've fitted these before and there is ample room to terminate a swa

also Table 7.1 in the OSG (17th) shows a 1.0/1.0 cable being as satisfoctory on a 10A MCB. Max circuit length 35 metres, if new ref methods 101,A, 100,102 or C are used

 
Thanks guys for your prompt replies. Seem to get good reports so think will get one and try. Incidentally the price seems to vary from

 