A bit of a follow up.....I know that the NICEIC do not like what they would class as "live work" but they are barmy... How can you properly establish what Zs is, unless you know what Ze is, and you will HAVE to test that live..
I will tell you a little story.... When planning these things, it might be better to play on the "safe side" as it were, and just say you arrived at a figure for Ze "by enquiry" and add R1 + R2 to that, as, then, at least you know, that if over the years Ze creeps up due to deterioration of the DNO installation, that, at least you are covered...
The trouble is,
Firstly, if you did that, you would not be able to meet disconnection times [in theory] in a lot of the jobs you do, [as your "theoretical" Ze would be so high to start with] and;
Secondly; "at least you are covered" but are you?????
Well, no, definitely not.... It would be nice to be able to say that "well, i know that R1+R2 are low enough in "my bit", and so, if the DNO allow Ze to go over the limits, then they are responsible.
Trouble is, they are not limits.. All this stuff you read about TNS .8 ohm and TNCS .35 ohm are only guidelines, illustrations if you like. The actual figure can be higher, and the DNO's freely point this out, so you MUST get the figure by testing.. The only figure i think that they HAVE to observe, is the Ra for their rod at the transformer end of the supply [21 Ohms]
Anyway, back to the little story i was going to tell you.. About a year ago i had a new supply installed to my shed. [3 phase TNCS] Firstly, they turned up with the wrong size cable, [but they would not admit it] and it was only after i said "look, that is the cable size on the quotation, the planners do not arrive at cable sizes by guessing, i do not care what is on your job sheet" that they went and got the right size. Once they got the right cable they discovered the "new" bit was 2 feet too short.....
Anyway, they got it all installed and off they went. A few months later, having bought my new MFT, i had a bit of a play with it. I thought i would test Ze on my new supply. One phase was .52!!!!!! on TNCS!!! I did not know what do think.... My main concern was that as this was obviously a problem with one conductor in the service cable, and that as i loaded it up, there would be more and more of a divergence in phase voltages, and that it would damage my motors. What was worse, was that purely by chance, the faulty phase was L2, the same phase as the house is on, but when i measured in the house, i got a sensible reading...
One day, a few days later, the DNO were working only a few hundred yards from where i live. I downloaded my figures for both the house and the shed, printed them out, and went and showed the DNO people. They came straight round, and guess what.....The cable jointers had forgotten to tighten the screws in the cut out!!!!! You could not make it up!!!
Sooooooooo, never ever rely on the figures the DNO give you, ALWAYS test, and if you are going to test Ze, then you might as well test Zs !!!!!!
john..